  • The turbo-generator fails in operation
    Service support - Product "Three Guarantees service" - Common fault handling

    Under the correct use and maintenance of the general turbogenerator, it is not easy to fail, but if the use and maintenance of improper, poor environment, disrepair, will also cause failure, the common causes of failure should be analyzed as follows:

     

    1) The output voltage of generator is unstable

     

    1.1) AVR control (normal when manual control) refer to AVR manual;

     

    1.2) Manual or automatic control, it may be due to other mechanical reasons in the system or the prime mover speed is unstable;

     

    2) The output voltage is too high, check whether the voltage reading meets the AVR requirements, refer to the AVR manual.

     

    3) Generator excitation failure

     

    3.1) If the excitation is normal under manual control and abnormal under AVR control, refer to the AVR manual and check the relevant connections;

     

    3.2) When there is no excitation current under manual or automatic control, check the circuit between AC exciter and rotating rectifier and AVR, and check whether the lead of rotor coil is open;

     

    4) The vibration of the generator is large

     

    4.1) Electrical: short circuit or grounding of rotor coil between turns, uneven air gap, deformation and displacement of rotor coil, damage and loosening of insulation of stator core;

     

    4.2) Mechanical aspects: the rotor is unbalanced, the center of the generator is not properly matched with the turbine, the gap between the bushing and the shaft is not uniform, the oil is short or the bearing fixing screw is loose, the foundation is not firm, etc.

     

    5) The generator rotor moves axially in series

     

    5.1) The rotor position is tilted during generator installation;

     

    5.2) When the generator is running, the center of the stator and the center of the rotor do not coincide.

     

    6) Damage of stator core

     

    6.1) When the stator coil is broken down, the silicon steel sheet will be burned;

     

    6.2) Loose iron core due to poor manufacturing or rusting.

     

     

    7) Fault of stator coil

     

    7.1) The loosening of slot wedge or end pad causes insulation wear of winding;

     

    7.2) Insulation aging caused by overheating of stator winding due to excessive load or other reasons;

     

    7.3) Mechanical damage of winding insulation caused by sudden short circuit;

     

    7.4) Breakdown of winding insulation caused by overvoltage;

     

    7.5) Insulation damage caused by stator core relaxation;

     

    7.6) Poor welding of stator coil joint.

     

     

    8) Fault of rotor coil

     

    8.1) Insulation resistance drop due to dust accumulation at the end of rotor coil;

     

    8.2) The sudden unloading of the generator causes excessive speed of the generator set, resulting in the increase of excitation voltage, which exceeds the voltage of the generator rotor and causes insulation breakdown;

     

    8.3) Short circuit between turns of rotor coil or unstable grounding;

     

    8.4) Local overheating of the rotor due to unbalanced load or asynchronous operation;

     

    8.5) Excessive excitation current caused by generator overload and overheating;

     

    8.6) Bad contact of coil joint causes overheating and insulation aging.

     

     

    9) Bearing failure

     

    9.1) Due to poor insulation between the bearing bush and the shaft, the shaft current passes through the bearing, causing overheating and corrosion of the bearing;

     

    9.2) Bearing overheating due to lack of oil;

     

    9.3) Bearing oil leakage due to improper oil adjustment and poor sealing;

     

    9.4) The bearing center is not aligned, and the bearing bush is scraped.

     

     

    10) The cooler is faulty

     

    10.1) Cooler pipeline blockage caused by cooling water fouling;

     

    10.2) Water leakage and pipe rupture due to mechanical damage, corrosion and vibration of the pipe;

     

    10.3) Because the cooling water temperature is too low or because the external inflow of air with too much humidity, resulting in condensation on the surface of the cooler;

     

    10.4) Because the inlet temperature of the cooler is too high, the inlet water amount is too small, or the cold and hot air channels are short circuit, the outlet air temperature of the cooler is too high;

     

    10.5) Gaskets between the water chamber and the tube plate are aged and not tight.

     

     

    11) Overheating of the generator

     

    11.1) Overload operation of the generator;

     

    11.2) Short circuit of core or winding;

     

    11.3) Failure of air cooler or ventilation system.


    主站蜘蛛池模板: 韩国精品视频在线观看| 99re免费视频| 日本免费的一级v一片| 国产女人乱子对白AV片| 91久久另类重口变态| 天天躁日日躁狠狠躁人妻| 久热免费在线视频| 狠狠精品干练久久久无码中文字幕| 国产AV午夜精品一区二区三区 | 爱情岛永久入口网址首页| 国产大学生系列| chinese麻豆自制国产| 少妇激情av一区二区| 丰满少妇又爽又紧又丰满在线观看| 日韩欧美一区二区三区在线播放| 亚洲午夜在线一区| 欧美日韩一区二区三| 亚洲精品中文字幕乱码三区| 男人女人做30分爽爽视频| 再深点灬舒服了灬太大了在线观看 | 国产精品自在线拍国产手青青机版 | 宅男噜66免费看网站| 久久香蕉国产线看免费| 欧美影院一区二区三区| 亚洲无线一二三四区| 精品人妻无码区在线视频| 四虎免费大片aⅴ入口| 久久亚洲精品专区蓝色区| 天堂…中文在线最新版在线| 久久久久99精品成人片试看 | 午夜私人影院免费体验区| 美女裸体a级毛片| 四虎永久免费网站免费观看| 色偷偷人人澡人人爽人人模| 国产乱码精品一区二区三区中| 风间由美性色一区二区三区| 国内外成人在线视频| 99国产精品久久| 在线观看欧美国产| 99re免费99re在线视频手机版| 在线看欧美成人中文字幕视频|